Would using closed cell foam be wrong in that it creates a vapor barrier?
- Windows on Washington
- Posts: 4868
- Joined: Wed Apr 04, 2007 11:21 pm
- Location: DC Metropolitan Area-Maryland/Virginia/DC
- Contact:
Re: Install Question
Negative anthony. CC SPF is a class II vapor retarder at most of the depths it will be installed.
The other lack of a concern in this case is that the CC SPF is also a complete air barrier. Stopping the air = Stopping the moisture so the point is largely moot at that point.